Yes, the end goal here would be to minimize any noise getting out through the equipment power lines. The SSR controls a heater load, that is time proportioned over a 2 second period. The most it will turn on and off over a 2 second period would be 1 time.
For my sub panel I have line voltage (typically 230V or 480V), separate 110VAC, 24VDC, and some RS485, RS232, and Ethernet communications. My number one area to minimize noise would be the communications wiring. After that would actually be the noise that is getting out on my power lines.
Twisting all of the 110V wires together would definitely decrease the noise on the wires, but not really a concern right? I don't think it would decrease the noise going out on the wires. For my power supply, which takes the 110V as input and gives me a 24VDC output, I would want to minimize the noise coming in on that particular wire because it will affect the 24VDC output?
As for my 24VDC, would I want to twist together all of the V+ and V- wires together to reduce common mode noise?