It is my understanding that a zero sequence CT is typically used for ground fault sensing and can be used to detect a ground fault on a circuit by summing the current on the three phase legs. These currents under normal operation will vectorally sum to zero, however with a ground fault, since some current will go to ground and not return on the other phases the CT will see this imbalance and send a current signal to a relay. Is this correct?
Understaning this, my question comes in as to weather or not a zero sequecne will sense an unbalanced load? Can a zero sequence trip a relay due to an unbalanced load or strictly from a ground fault? I have been told that with an unbalanced load the total current going into the CT is coming back on the other phases so it should still some to zero? Is this correct? Can someone ellaborate any further?
Thanks
Understaning this, my question comes in as to weather or not a zero sequecne will sense an unbalanced load? Can a zero sequence trip a relay due to an unbalanced load or strictly from a ground fault? I have been told that with an unbalanced load the total current going into the CT is coming back on the other phases so it should still some to zero? Is this correct? Can someone ellaborate any further?
Thanks