We have some magnets connected to a 500 V dc power supply. The magnets have exposed power leads and they cannot be accessed while in operation. We plan to install on each magnet a UL Listed Universal Power Alert device UPA-100 (http://www.alliedelec.com/Images/Products/Datasheets/BM/ATC/ATC_Industrial-Control_9930006.pdf) that indicates if the voltage is less than 27 V.
When we want to perform maintenance on these magnets we shut off the power supply, apply Lock and Tag and perform a Zero Voltage verification required by NFPA 70E since the equipment operates at >50 V. If the UL Listed UPA-100 indicates <27 V we can do the zero voltage verification with minimal training and PPE.
Question: if the UL Listed UPA-100 indicates <27 V, can we consider the equipment as if it operates at <50 V so that we are not required to perform the zero voltage verification?
When we want to perform maintenance on these magnets we shut off the power supply, apply Lock and Tag and perform a Zero Voltage verification required by NFPA 70E since the equipment operates at >50 V. If the UL Listed UPA-100 indicates <27 V we can do the zero voltage verification with minimal training and PPE.
Question: if the UL Listed UPA-100 indicates <27 V, can we consider the equipment as if it operates at <50 V so that we are not required to perform the zero voltage verification?