The use of a grounding transformer is necessary when one inherits an ungrounded system and you want a way of providing a ground point on the system and protecting your installation from ground faults as well. But, you have the choice to either solidly ground it or employ low-resistance, high-resistance, or reactive impedance grounding! I had that experience in my green years where our ungrounded 6.9kV feeder line made up of stranded Cu wire was broken (or intentionally cut) which resulted in a fatality--> the feeder breaker did not trip and the line was on the ground; a person accidentally (or intentionally, as in wire thievery) touched the live line and died. I was the one who helped calculate the needed grounding transformer, why I replied to this post.