I have posted several messages on this topic, and am happy to report that I am finally rid of that monster. The electrical contractor replaced it yesterday, and resolved a number of minor problem areas throughout the house. But he didn't have time to get to everything.
One item he didn't get around to is to install a GFCI breaker (2-pole) for the branch circuit feeding the hot tub. Afterwards, we discussed this, and I'd like opinions on what he told me.
He said that the circuit only had two hots and an EGC (no neutral wire). Apparently, all heater and motor loads must be 240 volt, and the tub's lights must be fed by a step down transformer. He then said that he could not hook up a GFCI breaker, because there would be no way to connect the neutral pigtail attached to a GFCI breaker.
I would think that a GFCI breaker would operate properly, even without a neutral connection. Any difference between the current in the two hot wires should cause a trip. Should I call him back in to change out the breaker, or would it be of no use?
One item he didn't get around to is to install a GFCI breaker (2-pole) for the branch circuit feeding the hot tub. Afterwards, we discussed this, and I'd like opinions on what he told me.
He said that the circuit only had two hots and an EGC (no neutral wire). Apparently, all heater and motor loads must be 240 volt, and the tub's lights must be fed by a step down transformer. He then said that he could not hook up a GFCI breaker, because there would be no way to connect the neutral pigtail attached to a GFCI breaker.
I would think that a GFCI breaker would operate properly, even without a neutral connection. Any difference between the current in the two hot wires should cause a trip. Should I call him back in to change out the breaker, or would it be of no use?