There were a few main problems with Zinsco products that I noticed: the attachment spring was sometimes looser than it should have been for full contact; the aluminum bars changed physically to a less conductive and "coated" or oxidized state once overheated (or even heated ); and the breaker style seemed to trap heat near the attachment screws or at the attachment clip, damaging nearby breakers as well as the overheating breaker.
The panels seemed barely adequate for wire spacing in the 20/40 slim panels. It seemed that all the wires would have to pass thru one location.
I have repaired panels with new bars and always re-adjusted the spring clips by forcing them closed before re-installing. As far as I know, most of the panels that I repaired in this fashion are still operating unless remodels created need (or opportunity) for updating the panel, for size, parts availability, and used equipment restrictions. Some jurisdictions did not like relocating panels, saying they were "used". This may merely been a way to get rid of Zinsco and fedpac panels.
The main problem seems to be the overheating/fires liability with less than meticulous installations.
paul