Zinsco Switchboard AIC rating?

Status
Not open for further replies.

scotteng

Member
Location
Apollo Beach, FL
Occupation
Professional Engineer
Does anyone know if or how to determine the fault current rating on a Zinsco Switchboard if nothing is listed on the equipment? Is there anyone or any company that maintains records of the original fault current listings for FPE, FA, Zinsco, etc.?

Have a POCO replacing an XFMR and I need to "recertify" that the gear has an AIC to handle the new AFC when the utility does the XFMR replacement.

I am familiar with the issues regarding Zinsco gear and their buss/breaker problems. Just searching for any knowledge base on fault current ratings for existing obsolete gear.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Do you want the AIC of the breakers or the SCCR/ SCA Withstand of the switchboard? These terms are not interchangeable, although many in our industry do. AIC is addressed in NEC 110.9 and SCCR/withstand is under 110.10.

UL did not start testing, and therefore much of the industry did not start labeling, SCA ratings of switchboards and panelboards until around the mid-80's. Prior to this you would need to find the original factory drawings/specifications.

Breakers were available with AIC ratings up to 65k and higher as far back as the 50-60's.
 