Zip cord for 12v lighting

Status
Not open for further replies.
Does it fit either of the below.

411.4 Specific Location Requirements .
(A) Walls, Floors, and Ceilings.
Conductors concealed or extended through a wall, floor, or ceiling shall be in accordance with (1) or (2):

(1) Installed using any of the wiring methods specified in Chapter 3

(2) Installed using wiring supplied by a listed Class 2 power source and installed in accordance with 725.130

Roger
 
Thanks Roger:D

You may well not be so thankful after you figure out the answer if you already ran the wiring. :)

BTW, what applications would article 720 typically involve. It seems fairly obvious until one digs into it does not apply to most low voltage (<50V) circuits.
 
Last edited: