JJspark
- Denver, Co., U.S.A
May you use zip ties to support LFMC. What is code article?
what code article says the zip ties have to be listed as supports?
350.30 Securing and Supporting. LFMC shall be securely
fastened in place and supported in accordance with
350.30(A) and (B).
(A) Securely Fastened. LFMC shall be securely fastened
in place by an approved means within 300 mm (12 in.) of
each box, cabinet, conduit body, or other conduit termination
and shall be supported and secured at intervals not to
exceed 1.4 m (41?2 ft).
Approved. Acceptable to the authority having jurisdiction.
Even UV-resistant nylon zip ties will fail in short order (within a few years) if installed in a location where they are exposed to direct sunlight.if used outside, at the very least those ties should be weather and UV-resistant.
Maybe.
Does the word "approved" refer to the strap/device/equipment... etc or it is referred to "AHJ must approve the device/strap/equipment?
I don't know but my understand is if the zip tie is approved to hold pieces together then it is ok to use it as a strap. For example electrical tape is not approved hardware to be used as a strap.
I don't but that's cuz I'm a cheapskate and would use tie wire.May you use zip ties to support LFMC. What is code article?