I had an inspector tell me he failed a job the other day because the pool installer/electrician drove a ground rod at the pool area and connected it in with the bonding grid.

My reading of 680.26(B) suggests that while driving a rod is not required, it is permitted. What are your thoughts? Thanks. :)
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
My thoughts are the same as yours---that's scary-- What is the difference between bonding to a ground rod or bonding to an equipotental grid or the pool steel.

I see no problem with it but I agree it is unnecessary.
 

JohnJ0906

Senior Member
Location
Baltimore, MD
I had an inspector tell me he failed a job the other day because the pool installer/electrician drove a ground rod at the pool area and connected it in with the bonding grid.

My reading of 680.26(B) suggests that while driving a rod is not required, it is permitted. What are your thoughts? Thanks. :)

What was his reason for failing the instalation?
 

electricalperson

Senior Member
Location
massachusetts
I had an inspector tell me he failed a job the other day because the pool installer/electrician drove a ground rod at the pool area and connected it in with the bonding grid.

My reading of 680.26(B) suggests that while driving a rod is not required, it is permitted. What are your thoughts? Thanks. :)

driving a rod does nothing since all the wire, rebar if used, and the big ufer ground if theres a concrete deck installed is probably lower resistance than the rod. it does not create more of a danger unless he was thinking that driving a rod might hit some underground utility or something
 

ibew441dc

Senior Member
I had an inspector tell me he failed a job the other day because the pool installer/electrician drove a ground rod at the pool area and connected it in with the bonding grid.

My reading of 680.26(B) suggests that while driving a rod is not required, it is permitted. What are your thoughts? Thanks. :)

I'm curious.....Did he site you a specific violation....or even something close for that matter??

Or was it one of those. ":mad:Fix or else's I'm the AHJ" or maybe ":mad:the code says it is , and its not my job to educate you"

From the info gathered I would offer the suggestion that it is permissible:smile:
 

wbalsam1

Senior Member
Location
Upper Jay, NY
I'm curious.....Did he site you a specific violation....or even something close for that matter??

Or was it one of those. ":mad:Fix or else's I'm the AHJ" or maybe ":mad:the code says it is , and its not my job to educate you"

From the info gathered I would offer the suggestion that it is permissible:smile:

No, he didn't cite a code violation specifically, but I remember him mentioning that it was in the code. I haven't been able to find it, though. :-?:smile:
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
He claims it's against the code. But, I haven't been able to find where that's true. :)

It could be 680.26(B) but if it is, he is misinterpreting it.

(B) Bonded Parts. The parts specified in 680.26(B)(1) through (B)(7) shall be bonded together using solid copper conductors, insulated covered, or bare, not smaller than 8 AWG or with rigid metal conduit of brass or other identified corrosion-resistant metal. Connections to bonded parts shall be made in accordance with 250.8. An 8 AWG or larger solid copper bonding conductor provided to reduce voltage gradients in the pool area shall not be required to be extended or attached to remote panelboards, service equipment, or electrodes.
 