why must you install a disconnecting means ahead of main breaker ie disconnect at meter when installing a generator ive always done it only because i know it has to be done but what is the reason behind it?
What if the generator has an OCPD at the generator and when you enter the bldg. you terminate in a transfer switch, in an OCPD still required??
Bob, On a typical residential install with a generator & automatic transfer switch, do you feel the circuit breaker on the generator (detached from the residence) can serve as the required disconnect (such as in 225.32) or must there be a disconnect on or withing the residential structure.What part are you having trouble with?
The basic idea is that anyone service the building supplied by the generator can open the circuit and place a lock on it so that they can safely work on buildings wiring systems.
Bob, On a typical residential install with a generator & automatic transfer switch, do you feel the circuit breaker on the generator (detached from the residence) can serve as the required disconnect (such as in 225.32) or must there be a disconnect on or withing the residential structure.
Their reasoning was. The breaker on the generator was not service rated and it was not readily accessible due to having to remove a cover to access the breaker. The question was then ask "what if the cover had a window to access the breaker with out removing any thing"? Their answer still reverted back to the breaker not being service rated.
All of this is correct. Yes, the genny would start, which is why it also must have a means of disconnect. You now have two sources which need disconnectability.the way ive done this in the past is the feed from meter goes to disconnect then load side of disconnect goes to xfer sw then distribution panel is fed from xfer sw. so if you were to shut off main disconnect, wouldnt that show as a power outage causing gen to start? so you also would need to turn off breaker at gen (power source)
Curtis, I have purchased generators with service rated OCPD/disconnecting means, the most recent was a 250 kw Onan, this requirement was included in the job specs.
Roger
On a typical residential install with a generator & automatic transfer switch,