The leakage comes from one main component; the unbalanced architecture of the single phase 120 volt circuit with line being referenced to ground. This causes capacitive coupling of 60 Hz current into the EGC when ran with their circuit conductors.
Common misconception. Do the math on the capacitive reactance and circuit impedance at 60 Hz and even at many KHz, and you'll see that wire to wire capacitance and even "filter" capacitors don't really enter the picture until you get up to RF.
I quite agree that the "protected" equipment is itself partly to blame for ground noise, mainly due to switch mode power supplies and such. However the mechanism by which it enters the ground is not just capacitive, but inductive coupling from the CCCs, as I've stated earlier.
By using an isolated EGC only bonded only and the N-G bond instead of using the lower impedance ground plane of the conduit and building only mitigates the problem.
The isolated EGC is more susceptible to ground voltage induction if the CCCs aren't oriented properly with respect to the EGC. The coaxial nature of conduit is both less susceptible to ground voltage induction and lower impedance when all fittings and connections are new and tight. However I would argue that over the lifetime of the system, the copper ground wire will maintain a better ground connection.
One is using a completely different power architecture ... balanced power
The second method used is just a good ole fashioned isolation transformer
I agree about using an isolation transformer, and I spec them into quite a few of my systems. Balanced power, however, is a solution in search of a problem. When applied into a situation with many other problems it can sometimes mask them enough to present an impressive improvement. It's proponents seem to miss the fact that it is inherently an isolation transformer and would offer the same improvements if the output were unbalanced instead of balanced. Couple that with the GFI and other requirements, makes it less than ideal. It comes back again to the fact that it's really not the capacitive imbalance that's the problem.
However today it is becoming a moot point because IGR is antiquated because most all low level signal transmission is now being done with balanced signals, digital, and optical transmission methods.
I quite agree that in the future these issues will be minimized because of digital and optical signal transfer. However today it is still an issue and it's worse than a decade ago because high harmonic loads are everywhere. Wall Warts are all becoming switchers now, CFLs are particularly nasty, dimmers are everywhere and built way too cheap. It's all about current waveform risetime, and those big heavy coils of wire that slow things down are the first victims of cost cutting. So ground noise today is a lot more of high narrow spikes than it was years ago. Since electronically balanced signal interfaces reduce their usable signal headroom by whatever (peak) voltage they need to cancel, these ground noises are more troublesome than in the past.
And here I thought I was going to try to stay out of IG arguments.:roll: