Big Guns

Member
with a 3 phase system can you share the same netural with 3 individual GFCIE breakers or do you have to run seperate neturals
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
You can use GFIs on a MWBC. They only check for leakage on their load side, not line. Or am I wrong?
Yes, you can use gfci on a mwbc but you cannot use individual sp Gfci snd link them together. It must be a DP or 3P Gfci breaker depending on your MWBC
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
If we are talking GFCI breakers, not GFPE, does anyone make a 3 pole GFCI ?
 