Is a mechanical room in a finished residential basement a non-habitable room and require GFCI protection for receptacles that serve circulation or boiler pumps according to NEC 210.8?
look at 210.52(G)
IMHO a receptacle in a mechanical room in a finished basement does not require GFCI protection.
Chris
Where does that address the GFI question?
I think that regardless of what you call the space if it is a dwelling unit basement and is unfinished it needs GFCI protection. Call it the laundry room, the mechanical room, the play room, the looser sons bedroom, etc it is still basement.
what is classified as un finished?
IMO if its a laundry room , office, bedroom in the basement I could consider that finished. unfinished to me is bare concrete walls open ceiling joist. what is the IRC or IBC definition of unfinished basement
If the mechanical room is unfinished GFCI protection is required regardless of condition of the rest of the basement.
210.8 A5
I agree, but what determines an unfinished mechanical room?
The building codes do not require a mechanical room to be sheetrocked, painted or have any other floor coverings than the raw concrete.
Chris
Not relevant. The question is, "what determines an unfinished basement (or portion thereof)"?I agree, but what determines an unfinished mechanical room?
That is not how the code defines it. The phrase "unfinished basement" is defined as being not intended to be habitable and being limited to storage or a work area.IMO, lack of floor and wall finishes even when not required means it is an unfinished room.
IMO, lack of floor and wall finishes even when not required means it is an unfinished room.
I take 'unfinished' to mean no wall , floor or ceiling 'finish' I do not believe they mean 'incomplete' as in a work in progress.
Is a mechanical room in a finished residential basement a non-habitable room and require GFCI protection for receptacles that serve circulation or boiler pumps according to NEC 210.8?
...........Perhaps we should explore 210.63?
This topic got derailed real quick.
Perhaps we should explore 210.63?
IMO, lack of floor and wall finishes even when not required means it is an unfinished room.
I take 'unfinished' to mean no wall , floor or ceiling 'finish' I do not believe they mean 'incomplete' as in a work in progress.