This is just an opinion, but I don't think one substation feeding a building was intended to be considered as "more than one building or other structure." ...
Maybe. Article 100 is pretty clear on the definition of "structure".. Most smaller stuff I have seen, like a 1000kva pad-mount with an intergal HV disconnect, has a full sized secondary run to the main building where the secondary OCP is located. Then the building has a switchboard with feeders running off to other parts of the building. There are rarely a half-dozen feeders from the pad-mount to various parts of the building.
I suspect it is cause the fire department wants one location where they can shut off the power.
...Again, just an opinion, but I think the intent was intended more for multiple structures that use electricity. You don't usually want multiple feeders to one building from multiple other places. ...
Yes that too. Same reason.
cf said:
Build a covered walk way between the substation and the building. This makes them one structure. Why that would make the installation any safer, I don't know. Even if it met code, it's nothing I'd ever want my name on.
...Why wouldn't you want your name on that? How is it any different than having the substation inside a room connected to the building? ...
It would look like I was trying to shave nickels building a marginal code compliant install. I don't like marginal. Always makes me wonder what else got shaved or "value engineered" to near un-workable
So the fire department shows up and says, "Where's the electrical disconnect?"
"Well, there are 6 scattered around this 2 acre building, or down that walkway about 145' there is a main disconnect."
...Why was the substation designed to be outside the building?...
Here are some guesses:
Doesn't want the 69kv primary inside of the building.
Doesn't want to put a 5mva oil filled xfm in the building.
Doesn't want to have to build a concrete xfm vault in the building.
Footprint for an outdoor mounted substation cost a lot less than heated, covered, inside footprint.
Doesn't want to install equipment to reject the heat loading from the transformer.
...However, I think there also might be cases where this is a perfectly safe installation, and some common sense, or inspector discretion might be called for. An example might be where the substation is located pretty close to the building.
That's true. And the plans reviewer is calling it as 225.30 says.
And you are right about the distance. If it were 10 feet, that is a good case for a covered walkway, enclosing the secondary main, making it all one structure. But that also gets rid of the outside unlimited taps to the remote panels/switchboards.
225.30 gives methods to do what David has in mind. Just need to pick one. What the code is asking is not bad.
cf