I have an existing 480V 3phase 3wire Federal Pacific panel from which I am feeding a new 250MCA chiller. The breakers in this gear only come rated at 40C. How do I size the wire?
40 C is the ambient temp rating of the breaker, not the terminal rating.
The terminal ratings will be 75 C.
Bob, do even old FPE CB's have the 75? C rating?
rated over 100 A).Distribution and Control Equipment TerminationsMost terminals are suitable for use only with copper wire. Where aluminumA 75 or 90?C temperature marking on a terminal (e.g.,
or copper-clad aluminum wire can or shall be used (some crimp terminals
may be Listed only for aluminum wire), there is marking to indicate
this. Such marking is required to be independent of any marking on terminal
connectors, such as on a wiring diagram or other visible location. The
marking may be in an abbreviated form, such as ‘‘AL-CU.’’
Except as noted in the following paragraphs or in the general Guide Information
for some product categories, the termination provisions are based on
the use of 60?C ampacities for wire size Nos. 14-1 AWG, and 75?C ampacities
for wire size Nos. 1/0 AWG and larger, as specified in Table 310.16 of
the NEC.
Some distribution and control equipment is marked to indicate the
required temperature rating of each field-installed conductor. If the equipment,
normally intended for connection by wire sizes within the range 14-1
AWG, is marked ‘‘75C’’ or ‘‘60/75C,’’ it is intended that 75?C insulated wire
may be used at full 75?C ampacity. Where the connection is made to a circuit
breaker or switch within the equipment, such a circuit breaker or
switch must also be marked for the temperature rating of the conductor.
A 75?C conductor temperature marking on a circuit breaker or switch normally
intended for wire sizes 14-1 AWG does not in itself indicate that 75?C
insulated wire can be used unless 1) the circuit breaker or switch is used by
itself, such as in a separate enclosure, or 2) the equipment in which the circuit
breaker or switch is installed is also so marked.
I'm assuming that this is from the 2008 NEC. In the 1987 NEC there is no provision for 60/75? connections in 110-14. Since this is Federal Pacific equipment it likely predates the 1987 NEC so I wouldn't assume that it has a terminal rating of 75? based on the 2008 NEC. Just a thought.
I'm assuming that this is from the 2008 NEC. In the 1987 NEC there is no provision for 60/75? connections in 110-14. Since this is Federal Pacific equipment it likely predates the 1987 NEC so I wouldn't assume that it has a terminal rating of 75? based on the 2008 NEC. Just a thought.