Have recenly installed a transformer that is tripping the breaker upon energizing the transformer. Circuit Details are as follows:
Transformer is a 25kVA single phase transformer with a 480 primary to 240/120 secondary. Transformer primary OCPD is a 70A breaker located about 800ft away. Transformer primary feeders are a #2AWG sized to account for voltage drop.
Transformer secondary is feeding load center who's main breaker is open when energizing the transformer, so there is no secondary load. As soon as we energize the transformer the breaker trips instantly. We checked primary cables and transformer windings to ground with megger and they all seem to be clear.
We are thinking that either something is wrong with primary windings, or primary breaker is too small to handle the inrush. We believe primary windings are all correct but are going to re-check.
Do you think the 70A breaker is too small for inrush? The breaker is not-adjustable. When sizing primary breaker I usually take transformer primary current and then size cables for this value. (Except for voltage drop cases) Then for primary breaker I incerase 125% to account for voltage drop. Is this correct? Ignoring voltage drop, do you just use 100% of primary current for sizing feeders.
BTW, the breaker is a 3-pole breaker, on which we are only using to phases.
Transformer is a 25kVA single phase transformer with a 480 primary to 240/120 secondary. Transformer primary OCPD is a 70A breaker located about 800ft away. Transformer primary feeders are a #2AWG sized to account for voltage drop.
Transformer secondary is feeding load center who's main breaker is open when energizing the transformer, so there is no secondary load. As soon as we energize the transformer the breaker trips instantly. We checked primary cables and transformer windings to ground with megger and they all seem to be clear.
We are thinking that either something is wrong with primary windings, or primary breaker is too small to handle the inrush. We believe primary windings are all correct but are going to re-check.
Do you think the 70A breaker is too small for inrush? The breaker is not-adjustable. When sizing primary breaker I usually take transformer primary current and then size cables for this value. (Except for voltage drop cases) Then for primary breaker I incerase 125% to account for voltage drop. Is this correct? Ignoring voltage drop, do you just use 100% of primary current for sizing feeders.
BTW, the breaker is a 3-pole breaker, on which we are only using to phases.