You need to break it down. I would make a simple table if it was just for an office. Basically, it would read:
Lighting @ 125%-------- ____________KW
HVAC @ 100%-------- ____________KW
Equipment @ 100%-------- ____________KW
Signage @ 100% 1.2 KW
Miscellaneous @ 100% _____________KW
Water Heater @ 100% ______________KW
Count your receptacles as 180VA if they are general and put them with your misc. items. Put in your HVAC load, signage is always 1.2KW. Lighting isn't really supposed to be at 125% but just do it anyway. If you read the NEC it says to size the branch circuit for 125%, but some plan reviewers dont beleive that so I just gave in pretty much.
Add these up and divide by your voltage. The total should be a little bit higher then your panel schedule (because of the extra 25% due to lighting).
There are other calculations that are optional in the NEC. rather then taking your actual lighting load you would use I believe 2.0 VA/square ft, otherwise everything else is the same.
I use this type of calculations for offices all over the country.
I wasn't aware of that. Are you saying smaller then 125 gallons? Continuous use is anything that runs for greater then 3 hours. Water heaters are either on or off dependent on the thermostat, if the elements turned on for over 3 hours I think the water would boil out of the relief valve. Which sections considers it continuous?
You need to break it down. I would make a simple table if it was just for an office. Basically, it would read:
Lighting @ 125%-------- ____________KW
HVAC @ 100%-------- ____________KW
Equipment @ 100%-------- ____________KW
Signage @ 100% 1.2 KW
Miscellaneous @ 100% _____________KW
Water Heater @ 100% ______________KW
Count your receptacles as 180VA if they are general and put them with your misc. items. Put in your HVAC load, signage is always 1.2KW. Lighting isn't really supposed to be at 125% but just do it anyway. If you read the NEC it says to size the branch circuit for 125%, but some plan reviewers dont beleive that so I just gave in pretty much.
Add these up and divide by your voltage. The total should be a little bit higher then your panel schedule (because of the extra 25% due to lighting).
There are other calculations that are optional in the NEC. rather then taking your actual lighting load you would use I believe 2.0 VA/square ft, otherwise everything else is the same.
I use this type of calculations for offices all over the country.