ceb58
Senior Member
- Location
- Raeford, NC
Details 240v 1ph system. 60kw generator, 12kw UPS .93pf input .8pf output, 4ton A/C unit.
What is happening is when running under gen power the UPS will lock on to the power and work as should with about a 3.5 kw load. when the A/C starts ( not on UPS circuits) the UPS will drop reg. power and switch to batt. in a short time it will switch back to reg. power then the entire time the A/C is running the ups keeps switching back and forth from reg. to batt. The A/C when running is pulling about 40amps. The full load of the building, the communication equipment, and the A/C is pulling around 60 amps. What could be going on? The gen seems to be more than adequate to handle all the loads. I can understand the UPS droping out under A/C start up but not after it levels out.
What is happening is when running under gen power the UPS will lock on to the power and work as should with about a 3.5 kw load. when the A/C starts ( not on UPS circuits) the UPS will drop reg. power and switch to batt. in a short time it will switch back to reg. power then the entire time the A/C is running the ups keeps switching back and forth from reg. to batt. The A/C when running is pulling about 40amps. The full load of the building, the communication equipment, and the A/C is pulling around 60 amps. What could be going on? The gen seems to be more than adequate to handle all the loads. I can understand the UPS droping out under A/C start up but not after it levels out.