Next guess must be that the genset frequency is unstable, possibly with it being borderline low frequency for the UPS. Is this a mechanically governed genset? Does the genset sound like its running true or is it hunting?But after the A/C reaches its running amps the UPS still switches back and forth from normal to battery.
The genset seems large for the load; 60KW@240 is about 300A, and the load is stated at 60A - if thats the case I'd rent a loadbank and get the genset up to 70%-ish load and see what happens then.