100809-2023 EST
chris:
I have started an experiment with one of my freezers. Ambient is about 85 deg F, and I have performed a calibration of the freezer box. From the start of a warming phase to the start of another warming phase (in other words the ends of cooling phases) was 4.5 hours, and the consumption was 0.78 KWH. Thus, the average KWH per hour was 0.173 or average power was 173 W and assumed to be constant.
I added 1 quart of 70 deg F water at the end of the above test. Thus, at the start of a warming phase. This is about 2.1 #.
If it does not take too long I will get a rough estimate tonight, but the curve is not going down very fast. For you to run the experiment in your freezer I now suggest 1 pint to 1 quart. I put the water on a flat cooking pan with raised edges. Water is about 1/4 to 3/8 deep.
I am going to guess towards 1/4 to 1/2 KWH to cool the water to my average of about - 4 deg F..
Theoretically it should take about (70-32)*2.1 = 80 BTU, plus 144*2.1 = 302 BTU, and plus (32 + 4) * 0.503 * 2.1 = 38 BTU for a total of 80 +302 + 38 = 420 BTU. There are 3413 BTU/KWH. Thus to cool this water should take 420/3413 = 0.123 KWH. But the system is inefficient.
At the present I have been cooling for 1.5 hours. There was an inflection in the temperature curve indicating the the water is frozen and thus we are now below 32 deg F for the water. The compressor has been running continuously. This freezer has cooling coils on the under side of each aluminum shelf. There is no circulating fan.
At this point I have 0.46 KWH for 1.5 hours. Thus, so far the excess required has been 0.46 - 0.26 or 0.2 KWH.
See if there are any errors in my calculations.
.