IllinoisElectrician
Member
This is kind of a followup to my last thread. I am supposed to install a generator 10kw generator, the ATS will be fed by the utility from a 50A breaker off the main panel.
My predicament is, there are 18,332A in available fault current from the 75kw transformer that supplies this house (200A Service, 120/240 3W 1P). The transfer switch has a "Amps Withstanding" rating of only 10,000kA.. the next one that that will work that is 22.5kA is ungodly expensive.
My question: Is the available fault current at the feeders different than at the service? And, by feeding the ATS with a breaker that has a 22.5kAIC rating, does that mean it isn't a problem that I use a pan only rated to withstand 10kA? I'm assuming no, but I really don't understand why not.
Oh, and... can someone explain available fault current to me so I have a more fundamental understanding of it?
THANKS!