Is tape "listed" for this + an overheating question

Status
Not open for further replies.

DARUSA

Senior Member
Location
New York City
look to me a MWBC neutral is overloaded
The two left side breaker look like they are the same phase and the 2 on the right the other phase. 12/3 +MWBC + two breaker same phase= neutal overheating!!!
 

tommyrice

Member
overheated nuetrals

overheated nuetrals

i think it's probably red and black wires on same phase.this could happed with fpe wafer breakers if someone didn't know better
 

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
FPE? The breakers failed to trip on an overload, and the neutrals happened to be torqued worse than the ungrounded conductors, would be my guess.

Edit: I suppose the hots could look about the same, no photo of that.
 