A customer wants us to supply a small control station to control some motorized valves. The valve motors are 120V and probably in the 1/8 HP range, or smaller.
Can we use the switch contacts from an AB 800T selector switch to directly control the motors? The standard switch contacts from these selector switches are not HP rated. However, AB does have some contact blocks available that are HP rated.
If we add the padlocking attachment to the selector switch in such an arrangement is it sufficient to serve as the motor disconnecting means if we were to make it a 3 position selector (open-off-close) where it could be padlocked in the off position.
Would this arrangement suffice if the panel had to be UL listed?
Can we use the switch contacts from an AB 800T selector switch to directly control the motors? The standard switch contacts from these selector switches are not HP rated. However, AB does have some contact blocks available that are HP rated.
If we add the padlocking attachment to the selector switch in such an arrangement is it sufficient to serve as the motor disconnecting means if we were to make it a 3 position selector (open-off-close) where it could be padlocked in the off position.
Would this arrangement suffice if the panel had to be UL listed?