yired29

Senior Member
Would the following installation be a code violation?

120/208 3 phase 60 amp feeder with #6 THHN feeding a 42 circuit 150 amp main breaker panel load calcs are good at 60 amp OCPD and # 6. All terminations 75 deg.
 

ceb58

Senior Member
Location
Raeford, NC
Thats the way I see it as well. The 60 amp OCPD provides the protection. The only problem I could see is if the 150 amp OCPD in the panel was not listed for #6 wire.

Lug listing would be the only hold back. Other than the lug wire rating you could feed a 400amp panel with #12 on a 20amp DP breaker.
 
408.36 permits the installation the way you have explained it in your post.



408.36. Overcurrent Protection.
In addition to the requirement of 408.30, a panelboard shall be protected by an overcurrent protective device having a rating not greater than that of the panelboard.
 

Buck Parrish

Senior Member
Location
NC & IN
I agree it's allowed . An other way to do it . Take the main 150 out of the panel. Fill the space with a listed method.
Then install a 60 with a breaker clamp on the bus bar. Bring your service wires to it. Mark it MAIN.
Then you have a 150 breaker available for an emergency call some day.;)
 
I agree it's allowed . An other way to do it . Take the main 150 out of the panel. Fill the space with a listed method.
Then install a 60 with a breaker clamp on the bus bar. Bring your service wires to it. Mark it MAIN.
Then you have a 150 breaker available for an emergency call some day.;)

They are not 'service wires', they are feeder conductors. I do not believe you would call it a "MAIN" either.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
They are not 'service wires', they are feeder conductors. I do not believe you would call it a "MAIN" either.
Pierre if you leave the 150 main breaker in the panel it is probably marked main. I don't see where marking the breaker that turns off the entire panel a main is an issue-- please explain.
 

lakee911

Senior Member
Location
Columbus, OH
I agree it's allowed . An other way to do it . Take the main 150 out of the panel. Fill the space with a listed method.
Then install a 60 with a breaker clamp on the bus bar. Bring your service wires to it. Mark it MAIN.
Then you have a 150 breaker available for an emergency call some day.;)

That's another way to do it, but I don't know that its any better. If you have a fault after the second 60A, but before a branch, you don't know which 60A will trip.

Pierre if you leave the 150 main breaker in the panel it is probably marked main. I don't see where marking the breaker that turns off the entire panel a main is an issue-- please explain.

Most panels that I've seen come with a sticker labeled "MAIN" and a bunch labeled "SERVICE DISCONNECT." I've never been absolutely sure where they are to go...
 

Cow

Senior Member
Location
Eastern Oregon
Occupation
Electrician
I don't see any problem calling it a "main." What else would you call it?

If he was labeling it "service disconnect" then that would be a different story.
 