Here is what we have:
One generator serves a Distribution Panel at 277/480 volt. Individual 4W feeders are run from the DP to 3 pole ATS's in different buildings. The grounded conductor is bonded/grounded at each building. Have we not tied the grounded conductor to ground at several locations? Shouldn't we have used 4 pole ATS's? If so, ouch! We are considering installing a delta-wye transformer at each building so we don't need the grounded conductor at all from the generator or the building service. I am open to other less costly interpretations! And/or solutions.
Thanks,
Jim
One generator serves a Distribution Panel at 277/480 volt. Individual 4W feeders are run from the DP to 3 pole ATS's in different buildings. The grounded conductor is bonded/grounded at each building. Have we not tied the grounded conductor to ground at several locations? Shouldn't we have used 4 pole ATS's? If so, ouch! We are considering installing a delta-wye transformer at each building so we don't need the grounded conductor at all from the generator or the building service. I am open to other less costly interpretations! And/or solutions.