Two seperate sources, no transfer switch

Status
Not open for further replies.

qcroanoke

Sometimes I don't know if I'm the boxer or the bag
Location
Roanoke, VA.
Occupation
Sorta retired........
What code section prohibits this?
Have a situation where the customer has two 225 amp panels with each having a seperate
feed but they are both tied together by a breaker in each panel.
So what we have is a situation where one main breaker would always be off unless there is a failure of the primary feed then that breaker would be opened and the 2nd main would be closed to put the load on the back up feed.
Please I know how dangerous this is, so lets leave that out of it.
What code section can I beat them with and prove to them its a code violation
And a transfer switch is needed.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I will be glad if someone can tell both you and I that there is a Code section that address this at least to the extent of labeling, but I know of no such provision.
If they were fed from different services, most POCOs would have input, but if both are fed from feeders I know of no violation.
Proper legends and even a "lirk key" system would be well advised.
 

qcroanoke

Sometimes I don't know if I'm the boxer or the bag
Location
Roanoke, VA.
Occupation
Sorta retired........
I will be glad if someone can tell both you and I that there is a Code section that address this at least to the extent of labeling, but I know of no such provision.
If they were fed from different services, most POCOs would have input, but if both are fed from feeders I know of no violation.
Proper legends and even a "lirk key" system would be well advised.

They are services, not feeders I should have been more clear on that.
Probably should say that this is a building going in a poco sub-station. I know poco's can do most anything but we can't......
 
Last edited:

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Bob is Good !

I had not thought about the buss rating.
The arrangement would be a violation of 408.36.
In addition, I think you will find your POCO will prohibit the arrangement (backfeeding) with a Kirk-Key or similar means to prevent it.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
The installation of a Main-Main service is very common. There are many different methods that can be used to prevent a paralleling of the sources.

In fact, many residential loadcenters have provisions for field installing this type of service.
 

markstg

Senior Member
Location
Big Easy
What if both sources are 'normal'?

They probably both are Normal. Normally (pun not intended) a Utility to Utility ATS is used, where the load stays connected to the one that's hot, and doesn't retranfer when power returns to the Other Normal source if the source it is connected to is OK.
 

ceb58

Senior Member
Location
Raeford, NC
Mike, I would ask how is this system classified? If it is classified as 700 or 701 system then you could start with 700.1 or 701.2 They both state "these systems are intended to automatically supply................." Then 700.6 A or 701.7 A
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
In absence of a definite means to prevent (even brief) paralleling, I would suggest a close reading of the first paragraph of Section 110.9. Take careful note of where in the circuit the fault interrupting rating must be based; i.e., the line side of the circuit breakers. In parallel, neither breaker would ever actually have to interrupt the combined fault; they would only need to interrupt the single contribution of one source (Unless the fault were internal to a breaker ? but then all bets are off anyway :D). Some downstream OCPDs may need to interrupt the combined fault currents though.
 

markstg

Senior Member
Location
Big Easy
Mike, I would ask how is this system classified? If it is classified as 700 or 701 system then you could start with 700.1 or 701.2 They both state "these systems are intended to automatically supply................." Then 700.6 A or 701.7 A

From the description of the install by the OP, it is neither.
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
I know this is similar to what is done in large airports, but I think they use some means to interlock it whether it is automatic or manual such as a kirk key.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Beyond the "human" element involved to prevent back-feeding and general concern by most, I-Wire's reference to the buss rating and rbalex's insight into the AIC problem present to valid Code issues.

(Some days it's a pleasure to be here and see the knowledge exhibited)
 

BILLY101

Member
Location
Telford, Pa
Around here the utility Companies don't generally adopt the NEC for their distribution system.
Office buildings and such come under a different authority and the NEC is adopted.
The case in this thread doesn't detail how the (2) services are controlled. Possibly by discipline of which cutout is closed/opened at any one time.
Also utility Companies are painfully aware of backfeeds at all voltages.
My sense is this is considered safely manageable by trained personnel.

BILLY
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
Beyond the "human" element involved to prevent back-feeding and general concern by most, I-Wire's reference to the buss rating and rbalex's insight into the AIC problem present to valid Code issues.

(Some days it's a pleasure to be here and see the knowledge exhibited)

I think we hashed this out in another post a couple of months ago too.:)
 