GFCI for refrigerator

Status
Not open for further replies.

480sparky

Senior Member
Location
Iowegia
Because the NEC does not address open areas below the countertop. Only above the top.

What about wall areas under a ceiling? Under cabinets? Under sinks? Under shelves? Under coathangers? Under curtain rods?

IMHO if they believed that outlets were needed below a countertop they would have addressed that subject.

O is the operative letter here.... opinion. I'm simply asking where you get your opinion's foundation?
 
Last edited:

480sparky

Senior Member
Location
Iowegia
............. I believe the NEC is silent on this space so I could not require an outlet.

It is not silent on the issue. It is covered quite specifically in 210.52(A)(2)(1).

That section does not state anything about 'wall sections under countertops'. Nor is there an exception for a space between cabinets. There is 2' or more of wall space, measured along the floor, and unbroken by fireplaces, doors, and similar openings.
 
Last edited:

Jim W in Tampa

Senior Member
Location
Tampa Florida
Where is a door required? That area is for my recycling. Again let me remove all my cabinet doors. What then? Do my cabinets require a back?
What if I laid plywood on the floor and called it a rolling shelf?


I can not justify that. I believe the NEC is silent on this space so I could not require an outlet.

You justify it the same as you do any wall space. If it is there it counts regardless of use or not.
With a door I call it a cabinet
with out door I call it a shelf
with nothing I call it open space
if you put a board there I would call it a shelf but it is not there.
cabinets do not require a back to be a cabinet
If by calling it recycling you mean trash can I would NOT call it a break in wall space.
remove doors and i have shelfs
The space is real and must be called something so you tell me what it is. It is not a shelf,not an appliance and not a cabinet.

Now if I was the electrician and you said not required I would be happy.
But if i was inspector and wanted it then we have issues. Make it into anything to qualify as a break in space and I would sign it off.
 
Last edited:

jxofaltrds

Inspector Mike®
Location
Mike P. Columbus Ohio
Occupation
ESI, PI, RBO
It is not silent on the issue. It is covered quite specifically in 210.25(A)(2)(1).

That section does not state anything about 'wall sections under countertops'. Nor is there an exception for a space between cabinets. There is 2' or more of wall space, measured along the floor, and unbroken by fireplaces, doors, and similar openings.

If you have a cabinet or cabinets installed there is no wall to be measured along the floor.
 

480sparky

Senior Member
Location
Iowegia
If you have a cabinet or cabinets installed there is no wall to be measured along the floor.


No wall?
surprised.gif
How many kitchens have you been in during your life?
 

480sparky

Senior Member
Location
Iowegia
Well shoot. That'll save me a ton of money the next kitchen I do.

If there's no wall along the floor, there's no wall there at all. 210.52(C)(1) just went away! :roll:
 

tallgirl

Senior Member
Location
Great White North
Occupation
Controls Systems firmware engineer
None is blinder than he who refuses to see.

210.52 (B) (2) Exception 2:

(2) No Other Outlets The two or more small-appliance
branch circuits specified in 210.52(B)(1) shall have no other
outlets.
Exception No. 1: A receptacle installed solely for the electrical
supply to and support of an electric clock in any of the
rooms specified in 210.52(B)(1).
Exception No. 2: Receptacles installed to provide power for
supplemental equipment and lighting on gas-fired ranges,
ovens, or counter-mounted cooking units
.
 

jxofaltrds

Inspector Mike®
Location
Mike P. Columbus Ohio
Occupation
ESI, PI, RBO
210.52 (B) (2) Exception 2:

(2) No Other Outlets The two or more small-appliance
branch circuits specified in 210.52(B)(1) shall have no other
outlets.
Exception No. 1: A receptacle installed solely for the electrical
supply to and support of an electric clock in any of the
rooms specified in 210.52(B)(1).
Exception No. 2: Receptacles installed to provide power for
supplemental equipment and lighting on gas-fired ranges,
ovens, or counter-mounted cooking units
.

Must be another book like mine out there.
 

jxofaltrds

Inspector Mike®
Location
Mike P. Columbus Ohio
Occupation
ESI, PI, RBO
You mean yours prohibits you from installing a SABC receptacle behind an electric range too?!?

Hooray, we might get on the same page yet.

NO it does not. Are you saying that I am not allowed to provide it for possible future use?
Ever seen a rough-in for both? Gas and electric.

But if there's no countertop?

Wall space. Assuming no opening, door, etc.
 