The OP did say "200 amp main breaker with a calculated load of 179 amps". Why assume that there's a problem with the calculation?
I don't assume that there is a problem with the calculation. I am simply saying that the information doesn't tell us everything we need to know to answer the question.
Don't the words calculated load imply that both continuos and non-continuos loads have been considered or are we working from a new definition in this thread?
Yes, the words calculated load imply that both continuous and non-continuous loads are being considered: calculated load = continuous loads + non-continuous loads. The calculated load (per 220.40) is the sum of the loads on the branch circuits (as determined by Part II of Art. 220) after any applicable demand factors have been applied.
If you had a 3000 sf office building with 50 receptacles outlets, 220.40 would tell you your calculated load would be:
Lighting 3.5va/sf*3000sf = 10500va (continuous)
Receptacle 180va @ 50 = 9000va (non-continuous)
Total 19500va