arc flash at 208Y ?

Status
Not open for further replies.

jumper

Senior Member
I believe that 70E requires arc flash calculations are required on 208v systems fed by anything larger than a 112.5 kVA transformer.

That comes out to 312.5 amps, so you are past the limit at 600 amps.
 

the blur

Senior Member
Location
cyberspace
ok, I have some more details; and I am totally new to arc flash. We have a 600a service and a 400a service coming off a pad mount transformer. The KVA rating of the transformer is worn off. But it's obviously designed around a 1000amps for both services coming into the building. It's a 208Y/120 and the primary side is most likely 7.2KV.

My position is senior plant mechanic/engineer. There's a lot of sub panels which I don't worry about.

My concern is the 600amp panel, which we go into once a year to vacuum the dust out, and look things over. We were a wood shop, and now we are a packaging plant. Still very dusty... The 600amp panel is about 50 feet from the pad mount, but is feed by parellel feeders. no doubt the fault current potential is there.

Do I need the full Nomex suit when going into the 600amp panel ? or is eye protection, and a good pair of gloves all that is necessary ?
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
The amount and type of personnel protective clothing and equipment is a function of the amount of energy that can be released during an arc flash event. You can't know how much current that will be, without performing a calculation.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Do I need the full Nomex suit when going into the 600amp panel ? or is eye protection, and a good pair of gloves all that is necessary ?
It is extremely unlikely that the incident energy at your service entrance equipment is <40 cal/cm?. Also, because this is the service entrance location you probably do not meet the footnotes that would allow you to use the 'task table'.
 

the blur

Senior Member
Location
cyberspace
Would you touch a 600a main breaker that has not been excerised in 25 years ?

In the practical world that we live in, what is practical to handle this task ?
meaning not shutting down an entire business, that runs a night shift, and weekend shifts, etc, etc.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Would you touch a 600a main breaker that has not been excerised in 25 years ?

In the practical world that we live in, what is practical to handle this task ?
meaning not shutting down an entire business, that runs a night shift, and weekend shifts, etc, etc.
You need to schedule an outage. There is no provisions in the OSHA rules that would permit you to do what you want to do, no matter what PPE you use. Also that breaker should probably be tested to see if it still works.
 

jumper

Senior Member
Would you touch a 600a main breaker that has not been excerised in 25 years ?

In the practical world that we live in, what is practical to handle this task ?
meaning not shutting down an entire business, that runs a night shift, and weekend shifts, etc, etc.

It is not practical when someone is hurt or dies. OSHA will fine you big time, not to mention a personal lawsuit.
 

the blur

Senior Member
Location
cyberspace
So shutting off the 600a main solves the entire problem, and I can work on the panel naked ?

not mentioning the 6 lugs (parellel feeds)on top of the main that are still hot, but behind a piece of card board.
 

tkb

Senior Member
Location
MA
And that requires a phone call to the poco to go inside the pad mount, and de-engerize from there.

OSHA does not accept the excuse of "it was inconvenient" or "it is going to cost money" when there is an investigation into an accident.
 

zog

Senior Member
Location
Charlotte, NC
Also that breaker should probably be tested to see if it still works.

NFPA 70E article 205.3 General Maintenance Requirements. Overcurrent protective devices shall be maintained in accordance with the manufacturers? instructions or industry consensus standards Maintenance, tests, and inspections shall be documented.

Informational Note: Refer to NFPA 70B, Recommended Practice for Electrical Equipment Maintenance, and ANSI/NETA MTS-2007, Standard for Maintenance Testing Specifications for Electrical Power Distribution Equipment and Systems, for guidance on maintenance frequency, methods, and tests.
 