Everything starts with the story:
Had a 15KW motor running a ring compressor on a VFD tripping, its faults were overcurrent related. I checked the normal things voltage and current in and out of the VFD. All voltage was as expected all three phase's were ballanced and ramped up as expected. Current was also ballanced.
Then I checked voltage and current at the Motor Junction Box, megged for ground faults, and checked for restance phase to phase between windings. I found ballanced voltage and current again. The motor megged good and restance was balanced phase to phase.
I then identified that the VFD was set up to provied 400VAC at 97HZ and FLA was set for 45A. The motor was a connected delta (low voltage 230VAC/45A). I noted that I could get the VFD up to 36Hz and I was at 45A. Like all good Electricians I tryed to identify a mechanical issue bearring or obstructed air flow in the ring compressor output. In doing this I removed the load of the compressor and the motor ran normal. Well having had VFD's have a week SCR or leaking Cap's I suspected the drive and replaced it.
The new drive was installed and the issue remained. Which lead me again to look at the motor. I noted it had been in a delta config I removed the shorting bars and rechecked restance and found a complete set of windings missing. Thus ballanced resistance now made sence. This is a first for me, I have never had all 3 windings open at once. ALSO a great lesson learned... The motor was acting like a 7.5KW motor and could no longer run the compressor.
So motor off to rewind shop.
NOW, the question.... I understand motors may be setup like this to provide better torque in the Volt/Hertz setup.
Is the intent of this setup to limit the Voltage to the low volt range(230VAC in my case) and never expect to arrive at the configured high voltage( 400VAC in my case)?
Since all motors have volts per turn limits in the windings, is this some trick used in the specific design by the EE to max out a known motor?
Had a 15KW motor running a ring compressor on a VFD tripping, its faults were overcurrent related. I checked the normal things voltage and current in and out of the VFD. All voltage was as expected all three phase's were ballanced and ramped up as expected. Current was also ballanced.
Then I checked voltage and current at the Motor Junction Box, megged for ground faults, and checked for restance phase to phase between windings. I found ballanced voltage and current again. The motor megged good and restance was balanced phase to phase.
I then identified that the VFD was set up to provied 400VAC at 97HZ and FLA was set for 45A. The motor was a connected delta (low voltage 230VAC/45A). I noted that I could get the VFD up to 36Hz and I was at 45A. Like all good Electricians I tryed to identify a mechanical issue bearring or obstructed air flow in the ring compressor output. In doing this I removed the load of the compressor and the motor ran normal. Well having had VFD's have a week SCR or leaking Cap's I suspected the drive and replaced it.
The new drive was installed and the issue remained. Which lead me again to look at the motor. I noted it had been in a delta config I removed the shorting bars and rechecked restance and found a complete set of windings missing. Thus ballanced resistance now made sence. This is a first for me, I have never had all 3 windings open at once. ALSO a great lesson learned... The motor was acting like a 7.5KW motor and could no longer run the compressor.
So motor off to rewind shop.
NOW, the question.... I understand motors may be setup like this to provide better torque in the Volt/Hertz setup.
Is the intent of this setup to limit the Voltage to the low volt range(230VAC in my case) and never expect to arrive at the configured high voltage( 400VAC in my case)?
Since all motors have volts per turn limits in the windings, is this some trick used in the specific design by the EE to max out a known motor?