I have an outdoor Class I, Div 2 area (refinery tank field) with a terminal box which includes a 2A fuse protected 15-pt termial strip. 4 3/4" conduits carry the wiring. Upstream from the box is a Class I, Div 2 rated hermetically sealed switch. NEC 501.105(B)(5) allows a general purpose enclosure for the TB w/o conduit seals.
The issue is the contractor used a Nema 7 rated enclosure for the TB and no conduit seals because of 501.105(B)(5). I think the installation is OK, just overkill with the Nema & box. The inspector wants conduit seals because of the Nema 7 enclosure.
The question: Is the NEC stating "general purpose enclosure" meaning what I'm thinking, that the TB could be any box rated for the outdoor environment like a Nema 4X instead of a Nema 7 and because of the switch upstream it complies with 501.105(B)(1)?
Al
The issue is the contractor used a Nema 7 rated enclosure for the TB and no conduit seals because of 501.105(B)(5). I think the installation is OK, just overkill with the Nema & box. The inspector wants conduit seals because of the Nema 7 enclosure.
The question: Is the NEC stating "general purpose enclosure" meaning what I'm thinking, that the TB could be any box rated for the outdoor environment like a Nema 4X instead of a Nema 7 and because of the switch upstream it complies with 501.105(B)(1)?
Al