Does anyone know if THHN is sunlight res?? I am curious if this insulation would be acceptable to use for service loop/service entrance installed in conduit?
I don't think there is any guarantee of it being sunlight resistant by code -- will be manufacturer specific. That said, just about all THHN I've seen in sizes 6 and larger have been sunlight and oil resistant. I used it in a service mast.
Plain THHN is not rated for wet location. THWN-2 yes and it is Sun light resistance!!
As was noted, it is manufacturer specific not all THWN-2 is sunlight resistant
I think we all use thhn to mean thhn/thwn since almost all of it is dual rated.Ok ,but can you use THHN in a wet location ? How it can be permited for service drop?
Ok ,but can you use THHN in a wet location ? How it can be permited for service drop?
UL Wire and Cable Marking Guide table regarding THHN/THHW sunlight resistance references note 35, which states, "A product evaluated for sunlight resistance is marked “SUNLIGHT RESISTANT”, “SUN. RES.” or "SR."No, what I am saying is a lot of THWN-2 in smaller sizes is not sunlight resistant.
You pretty much have to check every time, either read it from the wire or from a cut sheet.
Just curious but why THHN for the service? cost? Pipe size?
What would you use?:?
What's Al got to do with it? Insulation types being discussed here are available in both Cu and Al conductors.I'd use XHHW, but here we have to run the service in pipe and AL is a lot less than CU. $$$$$
I have never seen Al THHN and rarely see Cu XHH.What's Al got to do with it? Insulation types being discussed here are available in both Cu and Al conductors.
I've seen a lot of Cu XHHW (XHHW-2), and rarely see any Al anythingI have never seen Al THHN and rarely see Cu XHH.
I've seen a lot of Cu XHHW (XHHW-2), and rarely see any Al anything
Again, what's that got to do with it???