GeorgeB
ElectroHydraulics engineer (retired)
- Greenville SC
- Retired
We've beaten wiring step down transformers as step up transformers to death ... I'm not reopening that issue.
I was monitoring a system with pressure and flow transducers, with the associated motor current via a Fluke 1000:1 clamp-on CT and Action Instruments AC current to DC voltage signal converter.
My customer was interested in the differences we saw between that instrument and another clamp-on, and out of curiosity, he hooked up 2 more clamp-on meters. He was surprised at the (total 4 or 5%) variations over about a 2:1 change in current.
I was asked if there was a convenient way to create, in an electrical maintenance shop, an adjustable current carrying conductor up to about 200A for them to compare meters. I've not seen anything like this commercially.
Let's ASSUME I took a 200:5 common CT, made a single wire closed loop through the window, and hooked the 5A leads to a variable transformer with a resistive load and good quality AC multimeter. Would the single wire loop have a stable current approximately 40 times the 5A wiring current?
Are there commercial devices to accomplish this function?