Variable Frequency Drives

Status
Not open for further replies.

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Has anyone ever heard of using a drive with a rated current less than the FLA of the connected motor and using the drive limit the current by never allowing the motor to run at full speed?
 

Besoeker

Senior Member
Location
UK
Has anyone ever heard of using a drive with a rated current less than the FLA of the connected motor and using the drive limit the current by never allowing the motor to run at full speed?
You can but bear in mind that the motor magnetising current can be about 30% of full load current without the motor doing any work.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Has anyone ever heard of using a drive with a rated current less than the FLA of the connected motor and using the drive limit the current by never allowing the motor to run at full speed?

It is not an unusual practice to upsize motors that are used on VFDs. It is much less common than it once was.

I think that it is a dubious code thing to put a 10HP drive on a 15 HP motor though.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Someone raised the question of a 400 amp circuit and a 400 amp VFD with a chiller rated at 426 MCA.
 

kwired

Electron manager
Location
NE Nebraska
Someone raised the question of a 400 amp circuit and a 400 amp VFD with a chiller rated at 426 MCA.

Is the 426 MCA for a single motor or a multimotor piece of equipment? Likely the VFD itself is only going to drive a single motor.

426 MCA also is likely already taken 125% factor for continuous load, for at least the largest motor if a multimotor unit.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Is the 426 MCA for a single motor or a multimotor piece of equipment? Likely the VFD itself is only going to drive a single motor.

426 MCA also is likely already taken 125% factor for continuous load, for at least the largest motor if a multimotor unit.

Details are sketchy but from what I know it's a chiller with a nameplate of 426 MCA. I would assume a single motor since the control panel is set up for one single feed.
 
Details are sketchy but from what I know it's a chiller with a nameplate of 426 MCA. I would assume a single motor since the control panel is set up for one single feed.

Feeding an entire chiller unit WITH a control panel from an ASD? Usually you have control power transformers and other elements such as oil pump, oil heaters, etc also feed from the single feed to the control panels besides of the contactor for the compressor. You may also have multiple compressors. So you would 'insert' the ASD into the circuit where the compressor combination starter may have been. The control of the ASD is a whole other issue, especially with complex control sytems such as a chiller. I really would not attempt to do this without talking to the manufacturer of the chiller.
 

kwired

Electron manager
Location
NE Nebraska
Feeding an entire chiller unit WITH a control panel from an ASD? Usually you have control power transformers and other elements such as oil pump, oil heaters, etc also feed from the single feed to the control panels besides of the contactor for the compressor. You may also have multiple compressors. So you would 'insert' the ASD into the circuit where the compressor combination starter may have been. The control of the ASD is a whole other issue, especially with complex control sytems such as a chiller. I really would not attempt to do this without talking to the manufacturer of the chiller.

Exactly why I asked if the 426 MCA was for a single motor or multimotor piece of equipment. VFD that does supply more than one motor will need to be a situation where all motors run at same frequency at same time, and will all start, stop, accelerate, decelerate at same rate and at same time. All different loads you may run into in a chiller probably will not work out so well to supply from a single drive.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Feeding an entire chiller unit WITH a control panel from an ASD? Usually you have control power transformers and other elements such as oil pump, oil heaters, etc also feed from the single feed to the control panels besides of the contactor for the compressor. You may also have multiple compressors. So you would 'insert' the ASD into the circuit where the compressor combination starter may have been. The control of the ASD is a whole other issue, especially with complex control sytems such as a chiller. I really would not attempt to do this without talking to the manufacturer of the chiller.

I was thinking about that also. Right now we're working off of a one line diagram that shows a conduit to the VFD then another conduit to the chiller which seems odd for the reasons you've menitoned.
 
Exactly why I asked if the 426 MCA was for a single motor or multimotor piece of equipment. VFD that does supply more than one motor will need to be a situation where all motors run at same frequency at same time, and will all start, stop, accelerate, decelerate at same rate and at same time. All different loads you may run into in a chiller probably will not work out so well to supply from a single drive.

...and of course all motors must be the same size, speed and even model. Even then it is an iffy proposition, in other words not just cut-and-dry, need to look at the application, minimum desired speed, accuracy and certainly not expected to perform high precision synch drive, like turing two wheels of a gantry crane.
 

Cow

Senior Member
Location
Eastern Oregon
Occupation
Electrician
Has anyone ever heard of using a drive with a rated current less than the FLA of the connected motor and using the drive limit the current by never allowing the motor to run at full speed?

That just seems really odd.....:? Wouldn't you want a fullsized drive anyway just so it isn't working so hard?
 
That just seems really odd.....:? Wouldn't you want a fullsized drive anyway just so it isn't working so hard?
  1. Motors are seldom loaded to their nameplates.
  2. Chillers/Compressors are especially cyclical loads, going from virtually unloaded to over nameplate loading and then unloading.
  3. Since the ASDs are thermally sized to continuous load and have typical overload capability of 10%(normal duty) or 50%(heavy duty) for one minute within a ten minute cycle. (that is allowing the motor to load to 100% for the remaining 9 minutes.)
So given the fact that the 426A was for the entire panel, it is conceivable that the compressor FLA or MCA is closer, if not below the available drive's 400A rating.
 