The title says it all. I'm confusing myself trying to figure out all of the proper grounding connections for a wye-wye service transformer that will by owned by the customer, not the utility. This is an outdoor padmounted transformer that will feed a switchboard inside the building. Utility is 13.2Y/7.6kV grounded wye. Secondary is 480Y/277V. My questions are as follows:
1. Are both neutrals (primary and secondary) typically connected to the steel case of the transformer and the grounding rods at the transformer? It seems to me like all of these connections would be bonded together inside the transformer.
2. If the secondary neutral is connected to the ground inside the service transformer (main bonding jumper connection), then the neutral and ground should be kept separate from that point on, correct? In other words, the connection from the neutral to the ground bus inside the switchboard should be removed.
3. Does the fact that this is a customer owned transformer change how these connections are made vs if this were owned by the utility?
1. Are both neutrals (primary and secondary) typically connected to the steel case of the transformer and the grounding rods at the transformer? It seems to me like all of these connections would be bonded together inside the transformer.
2. If the secondary neutral is connected to the ground inside the service transformer (main bonding jumper connection), then the neutral and ground should be kept separate from that point on, correct? In other words, the connection from the neutral to the ground bus inside the switchboard should be removed.
3. Does the fact that this is a customer owned transformer change how these connections are made vs if this were owned by the utility?