Thanks, I take it I would have to use the simpson for that, too small for amprobe. This has to be a huge problem in the northern USA, I am guessing most run an extension to a regular outlet.
Thanks, I take it I would have to use the simpson for that, too small for amprobe. This has to be a huge problem in the northern USA, I am guessing most run an extension to a regular outlet.
The way to actually test it is with a megaohmeter.
Are you sure you can do that?
I am not saying you can't but it seems to me that with heat trace being a semiconductor the readings would always look bad.
Where it goes bad is between the conductors and the shield, you have to meg between those. Any leakage there will show up as out of spec reading.
Here is a link to testing the cable by one manufacture.http://www.arcoengineering.com/chro/Chromalox_Heat_Trace_Testing_Procedures.pdf
Thanks, I take it I would have to use the simpson for that, too small for amprobe. This has to be a huge problem in the northern USA, I am guessing most run an extension to a regular outlet.
Not sure if it is a big problem. There is a lot of it plugged into GFCI receptacles without problems. The instructions for a lot of plugin heat tape calls for GFCI protection.
Thanks guys for all the good advice. Seems like a new deicing cable would work for a very short time until there is leakage
over 5ma
Insulation resistance testing (using a megohmmeter) should be conducted at three voltages; 500, 1000, and 2500 Vdc. Significant problems may not be detected if testing is done only at 500 and 1000 volts.
...A clean, dry, properly installed circuit should measure thousands of megohms, regardless of the heating cable length or measuring voltage (0?2500 Vdc). The following criteria are provided to assist in determining the acceptability of an installation where optimum conditions may not apply. All insulation resistance values should be greater than 1000 megohms. If the reading is lower, consult Section 10, Troubleshooting Guide.