130218-0841 EST
usman umar:
You have provided some clarification.
What is the reason for your questions?
What is your goal?
You did not define AVR, but it probably refers to automatic voltage regulator. The output voltage is controlled by the magnetic field intensity, and probably that is controlled by the excitation current to a wound coil type of field. Thus, you apparently plan to adjust field excitation to obtain a desired DC output voltage.
Ignore PF on a single generator. PF will be whatever it is, and thus determined by the load.
The 1.35 factor is correct for a full-wave bridge rectifier when the input voltage is a sine wave, voltage is RMS line-to-line of the delta source, the load is a pure resistance, and all series inductance is ignored.
Your ripple question depends upon the load, and internal series inductance of the generator. You need to define the load, and whether the source inductance is significant.
.