Lets say we have a microwave that is plugged in and is portable. It is a 20A branch circuit with a duplex receptacle. This means 210.23.A.1 is applicable with a max load of 16A.correct?
It also means 210.21.B.2 is applicable correct?
Now, Lets say we have a microwave that is plugged in fixed in place. It is a 20A branch circuit with a duplex receptacle. 210.23.A.2 is not applicable because there is no light fixtures and there is no other cord/plug portable loads. Therefore, per 210.21.B.2, the max load is still 16A (per table 210.21.B.2) correct?
What if there is a 20A branch circuit with a single receptacle (1 outlet; not duplex), could the microwave be a 20A max load? If yes, what if the connected load would be a continuous load like a portable heater? If it is say 19A load, the breaker would trip over time (continuous load).
Thanks
It also means 210.21.B.2 is applicable correct?
Now, Lets say we have a microwave that is plugged in fixed in place. It is a 20A branch circuit with a duplex receptacle. 210.23.A.2 is not applicable because there is no light fixtures and there is no other cord/plug portable loads. Therefore, per 210.21.B.2, the max load is still 16A (per table 210.21.B.2) correct?