I have a question i can't seem to find the answer to. Assuming a 480-120/208V 112.5 KVA Transformer is at full load, what would the heat rejection be ????? Would anybody know where to find this answer ???
You need to know its efficiency and power factor. Say its efficiency 95% and power factor is 0.9. Then its heat rejection would be 112.5x0.9x0.05=5.06 Kilojoules/second under steady state condition.Hi All,
I have a question i can't seem to find the answer to. Assuming a 480-120/208V 112.5 KVA Transformer is at full load, what would the heat rejection be ????? Would anybody know where to find this answer ???
You might want to rethink that.You need to know its efficiency and power factor. Say its efficiency 95% and power factor is 0.9. Then its heat rejection would be 112.5x0.9x0.05=5.06 Kilojoules/second under steady state condition.
You might want to rethink that.
I did??You have overlooked stating what the temperature rise is also which makes a very big difference.
In the absence of any better information I usually work it at around 2% for transformers.
Interesting that the table gives heat loss as BTu. You need to assume a rate to get power from that. So, now we have 2%, 3%, and 5%. And I didn't see where you took that all important temperature rise into account.Very useful link, you got.
@13,076 BTU heat loss, that would put the heat loss at 3.8 kW or about 3.37% ( I used 1 BTU/hr = 0.293 watts of electricity).
2% sounds more like a valid number. Actually I would expect it to be less than that so I would think 2% is on the conservative side. At least that is the case for utility distribution transformers.Anyway, this is where my 2% comes from
I did??
That statement has the implicit assumption that transformers are designed with the same parameters for an 80C rise as for a 150C rise.If you didn't what is the temperature rise of the transformer you are refering to? Unless it is your belief that doesn't affect the full load losses which it appears to be as such.
And am I to assume that "heat rejection" is with reference to heating wats of a fully loaded 112.5kva transformer which is commonly started as total lossed in watts which is the no load loss plus the full load loss. If so this value will be different for 150, 115, and 80 degc rise transformers.
That statement has the implicit assumption that transformers are designed with the same parameters for an 80C rise as for a 150C rise.
They aren't.
The one I quoted.If I implied what you said regarding "That Statement" which post of mine are you referring to?
The one I quoted.
Are you saying that they are not diffent but are the same??!!! How would that relate to my post #6?
If so this value will be different for 150, 115, and 80 degc rise transformers.