Q: The recommended size of Ground Loop Conductor buried around a building is usually 95-120sq.mm with 7-8 no.of ground rods bonded to it. I wonder how do they calculate this size and the number of ground rods? Thanks. gk
Q: The recommended size of Ground Loop Conductor buried around a building is usually 95-120sq.mm with 7-8 no.of ground rods bonded to it. I wonder how do they calculate this size and the number of ground rods? Thanks. gk
Q: The recommended size of Ground Loop Conductor buried around a building is usually 95-120sq.mm with 7-8 no.of ground rods bonded to it. I wonder how do they calculate this size and the number of ground rods? Thanks. gk
That is a substation grounding standard and would not really apply to the original question.According IEEE Std 80/2000
ch. 11.3.3 Additional conductor sizing factors
"In practice, the requirements on mechanical reliability will set the minimum conductor size. While it might seem proper for the designer to establish minimum sizes in light of local conditions, the need for conservatism deserves consideration."
4/0 awg [or 95 sqr.mm ] will be -from mechanical and corrosion point of view- an acceptable cross-section for stranded copper conductor [as a minimum if short-circuit conditions will required less].
Number of electrodes-if any required-depends on GPR level required. However, a minimum of 5-7 m distance between could be recommended.
Since you are using "sq mm" wire, I guessing you are not in the US. What code are you working to?
ice
You said recommended, recommended by whom? By the NEC a ground ring does not need connection to ground rods.
Q: The recommended size of Ground Loop Conductor buried around a building is usually 95-120sq.mm with 7-8 no.of ground rods bonded to it. I wonder how do they calculate this size and the number of ground rods?
According IEEE Std 80/2000, ch. 11.3.3 Additional conductor sizing factors. ...
Most project specification requires and as I understand ground rods are usually bonded to the loop around the building. Further it says-" you may add more rods in order to achieve the required ground resistance" say less than 5 ohms, similar to a loop around a substation where at least one rod is buried at each corner, attcahed to the loop.