My understanding of 210.21 is that you are allowed to use a 15A duplex receptacle as the only device on 20A circuit. This would be the only device connected to the breaker. The logic behind this is that a duplex receptacle has 2 points of contact (ref. receptacle definitions art. 100) and therefore meets the requirements of Table 210.21(B)(3). Any inspectors care to weigh in on if my interpretation is correct? Just to be clear, I don't agree with the practice of doing this and I am only asking if it is allowed by code.