I was wondering if I ran conduit in a straight trench how long does the run have to be before i need a pull box? I searched the 2011 NEC and couldn't find an article showing me the code



You either need one every hundred feet, two hundred feet or any length you want, if you have a vacume to suck a string through. The othe lengths are based on the lengths of your fish tape.

There is no rule.
 

Cavie

Senior Member
Location
SW Florida
You either need one every hundred feet, two hundred feet or any length you want, if you have a vacume to suck a string through. The othe lengths are based on the lengths of your fish tape.

There is no rule.

and just how froggy your feeling that day
 

Strathead

Senior Member
Location
Ocala, Florida, USA
Occupation
Electrician/Estimator/Project Manager/Superintendent
You either need one every hundred feet, two hundred feet or any length you want, if you have a vacume to suck a string through. The othe lengths are based on the lengths of your fish tape.

There is no rule.

If it is based on the length of many fish tapes it would be more like 185 feet. Just saying:)! One of my pet peeves!
 

Strathead

Senior Member
Location
Ocala, Florida, USA
Occupation
Electrician/Estimator/Project Manager/Superintendent
You need a slight extra length as it comes from the factory to allow for the length you burn off occasionally pushing it into a live panel. :)

I am used to idiots er...apprentices, cutting off 10 feet to use as a wall fish, (I am old enough that I lived before they had the fiberglass rods)
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
unlimited , you can go 800' with no junction box if you like, not a code violation
Now if OP is asking what is practical, he will not find that in the NEC. He could try asking members for their opinion on that question based on their experience. They will probably ask him about size of conduit, type of wire (including how much pull it can take without damage), and conduit fill factor.
 
Last edited:

kingpb

Senior Member
Location
SE USA as far as you can go
Occupation
Engineer, Registered
Apparently the posters have not heard of wiring pulling tension calculations.

The conduit run can be as long as you want it, provided the maximum pulling tension is not exceeded, which if exceeded will cause permanent damage to the cable.

A qualified cable installer will know how to perform those calculations.
 

mwm1752

Senior Member
Location
Aspen, Colo
Apparently the posters have not heard of wiring pulling tension calculations.

The conduit run can be as long as you want it, provided the maximum pulling tension is not exceeded, which if exceeded will cause permanent damage to the cable.

A qualified cable installer will know how to perform those calculations.


Do you know the fomula? Where would one find the calculation method. Sounds like a POCO job
 

JDBrown

Senior Member
Location
California
Occupation
Electrical Engineer
This conversation brings back memories...

A couple of years ago we designed a complete remodel of a commercial/industrial building with an existing 4160V service. We had one little section of new 5kV cables being run underground -- it was literally so short of a run that almost the entire thing was made up of two 48" radius elbows. And the Plan Checker made me put the calculations on the drawings. I felt a little bit like I was back in school -- "Show your work!" :rant:

The required pulling tension ended up being less than 250 lbs. -- just a bit less than the maximum allowed pulling tension 8,000 lbs. :D

Anyway, I used this publication from Okonite.
 