I have a RTU where phase to phase is 480V

Phase A to Grd - 813V
Phase B to Grd - 611V
Phase C to Grd - 317V

Rtu fed from 480V , 3P, 3W panelboard DP with an equipment groud

DP is fed from 500kva Delta 208V - 480VY step-up transformer. The feeder has (3) phase conductors and a ground.............No neutral

Ground voltages seem strange. What should they be? Where to look to correct? Seems like a grounding issue.

Thank you for your feed back
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
I have a RTU where phase to phase is 480V

Phase A to Grd - 813V
Phase B to Grd - 611V
Phase C to Grd - 317V

Rtu fed from 480V , 3P, 3W panelboard DP with an equipment groud

DP is fed from 500kva Delta 208V - 480VY step-up transformer. The feeder has (3) phase conductors and a ground.............No neutral

Ground voltages seem strange. What should they be? Where to look to correct? Seems like a grounding issue.

Thank you for your feed back

Sounds like you have an ungrounded 480Y/277 secondary and the voltage to ground readings you are getting are meaningless as there is no grounded reference, while the phase to phase are valid. The code would generally require this derived system to be grounded. There are exceptions, but probably not best in your application. See 250.20.
Also, be aware of the other requirements for this such as disconnecting means, overcurrent protection on primary and secondary, Grounding Electrode System, etc.
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
DP is fed from 500kva Delta 208V - 480VY step-up transformer.....
This right here makes me believe that this is what you are dealing with-
Sounds like you have an ungrounded 480Y/277 secondary and the voltage to ground readings you are getting are meaningless as there is no grounded reference.........
 

kwired

Electron manager
Location
NE Nebraska
I have a RTU where phase to phase is 480V

Phase A to Grd - 813V
Phase B to Grd - 611V
Phase C to Grd - 317V

Rtu fed from 480V , 3P, 3W panelboard DP with an equipment groud

DP is fed from 500kva Delta 208V - 480VY step-up transformer. The feeder has (3) phase conductors and a ground.............No neutral

Ground voltages seem strange. What should they be? Where to look to correct? Seems like a grounding issue.

Thank you for your feed back

As others have stated, sounds like the secondary is not bonded to ground. I bet if you connected any kind of load between any phase and ground you would change your readings, but there would not be enough power behind those voltages to drive the load. Those voltages are mostly the result of capacitive coupling. Testing with a low impedance meter will probably shunt enough current to have much lower readings.
 

Besoeker

Senior Member
Location
UK
I have a RTU where phase to phase is 480V

Phase A to Grd - 813V
Phase B to Grd - 611V
Phase C to Grd - 317V

Rtu fed from 480V , 3P, 3W panelboard DP with an equipment groud

DP is fed from 500kva Delta 208V - 480VY step-up transformer. The feeder has (3) phase conductors and a ground.............No neutral

Ground voltages seem strange. What should they be? Where to look to correct? Seems like a grounding issue.
Or the absence of one.
If the system isn't grounded at some point the readings with reference to ground could be almost anything and rather meaningless.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The OP says it is a 3 wire system...there is no code requirement for that to be a grounded system. There is a code requirement for the ungrounded system to have a ground detector.
 

Besoeker

Senior Member
Location
UK
The OP says it is a 3 wire system...there is no code requirement for that to be a grounded system. There is a code requirement for the ungrounded system to have a ground detector.
No disagreement with that. I was simply making the point that voltage measurements wrt ground are likely to be indeterminate on a system that isn't grounded.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
No disagreement with that. I was simply making the point that voltage measurements wrt ground are likely to be indeterminate on a system that isn't grounded.
True. I was responding to the comments that suggested that this system is required to be a grounded system.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Understood.
I can't work out from post #1 whether the transformer is Y input and delta output or vice versa.
It doesn't really matter as far as the code goes. Even if the output is wye, there is no code requirement to make a connection to the center point of the wye, unless you are using it as a circuit conductor.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
True. I was responding to the comments that suggested that this system is required to be a grounded system.

My concern is that if the secondary is wye there will be a neutral point at the source. Even though the system and loads may be 3 wire only, does the existence of a neutral point trigger the requirement that the neutral be grounded?
 

Besoeker

Senior Member
Location
UK
It doesn't really matter as far as the code goes. Even if the output is wye, there is no code requirement to make a connection to the center point of the wye, unless you are using it as a circuit conductor.
Even if you didn't need line to neutral voltage and code doesn't require it, wouldn't it be safer in most circumstances to ground the star point?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
My concern is that if the secondary is wye there will be a neutral point at the source. Even though the system and loads may be 3 wire only, does the existence of a neutral point trigger the requirement that the neutral be grounded?
Not for that voltage level. You have to ground it if it can be grounded so that the voltage to ground does not exceed 150 volts, so with a 480 volt system, it is not required to be a grounded system.
 

StarCat

Industrial Engineering Tech
Location
Moab, UT USA
Occupation
Imdustrial Engineering Technician - HVACR Electrical and Mechanical Systems
HVAC Common Failures

HVAC Common Failures

Ground faults are very " common " failures on HVAC machines. They happen often on fan motors, compressors, and yet still other ways.
I would be quite concerned about how the supply breaker will trip on phase to ground fault if the center tap on said transformer is not bonded to ground.
Even though the neutral point is not needed for service purposes, it would seem necessary to bond it in this case so the fault current returns to its source.
Please correct me if I am missing something here. This comes off like a potentially dangerous installation.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
I would be quite concerned about how the supply breaker will trip on phase to ground fault if the center tap on said transformer is not bonded to ground.
It would not, which is one reason that ungrounded delta systems are often used for critical industrial processes where an unplanned shutdown could be very expensive or dangerous. But for that same reason, an ungrounded system requires that the initial fault to ground be detected so that an orderly shutdown and repair can be done before a second fault occurs.
 

StarCat

Industrial Engineering Tech
Location
Moab, UT USA
Occupation
Imdustrial Engineering Technician - HVACR Electrical and Mechanical Systems
10-4

10-4

OK very good.
I would say the attending Electrician raised a solid concern.
Now, while a Plant Electrician in such a setting wil likely be aware of the possibility of live machine cabinets, a typical HVAC Tech called out to service a downed unit on such a system might not be aware.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
OK very good.
I would say the attending Electrician raised a solid concern.
Now, while a Plant Electrician in such a setting wil likely be aware of the possibility of live machine cabinets, a typical HVAC Tech called out to service a downed unit on such a system might not be aware.

There is no more likely hood of a "live" cabinet on an ungrounded system than there is on a grounded system.
 