Conductor Sizing For Meter Center

Status
Not open for further replies.

lawingnutz

Member
Location
Port Allen, LA
I am installing a new meter center that has a 600 amp bus and contains 4 separate meters each with 200 amp breakers. The service is single phase, 120/240V. The meter center is being installed in a mobile home community and will serve 4 separate mobile homes.

For incoming service I am planning to use parallel 350kcmil phase conductors.

What size neutral conductor(s) are required or recommended?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
The neutral conductor must be either full size or you must calculate the load. A standard rule of thumb for residential is to drop one size since there is plenty of 240 circuits with no neutral loads.
 
There are only about 3 code books on earth. The pope has one, NPR reporter Soraya Sarhaddi Nelson has one, and...........Ok thats enough, sorry Ive been in a goofy mood today. If you have a code book, you can look up conduit fill in Annex C. Generally dont go with the absolute minimum size unless there is a good reason. If you dont have a code book you really should get one. We would need to know what kind of raceway you will be using to give you an answer.
 