This make sense to me but 70%,
Can you explain me more in sense of "Potential difference" that neutrals create to attract currents in 120-277 volt loads.
what creates Pot. Diff. in 240-480v???
To what others have stated, I will add this...
Voltage is a measure of potential. Its the ooomph of the circuit. It can be likened to say a AA battery. It has essentially the same ooomph, sitting on the shelf in the store as it does installed in a flashlight (when still fully charged).
When you have multiple voltages in a system, it's like having more than one battery connected end-to end. Using a AA battery as an example, each has 1.5V potential. Connected together in series (the positive of one butted to the negative of the second), both together have a potential of 3.0V from the negative terminal of the first to the positive terminal of the second. Yet each battery still has 1.5V potential between its own terminals.
Potential difference, or rather difference in potential, doesn't really enter the picture until there are three points from which to make potential (voltage) measurements. If in the two battery example we choose to reference our measurements to the negative terminal of the first, this is saying that one of our meter leads (typically the black or negative lead) will probe this negative terminal for all measurements. Since there are only two other points (butt and second battery positive terminal) to make a measurement, we get measures of 1.5V and 3.0V respectively. Using these values, we can surmise the potential between the two points by taking the difference in potentials... 3.0V ? 1.5V = 1.5V.
While the preceding example is regarding DC voltage, split phase AC systems such as 120/240V and 240/480V exhibit basically the same relative RMS voltage measurement (though there will be no minus voltage measurement if you connect your meter leads backwards).
With 3? 4-wire systems, or 3-wire systems originating from them, the measurements will give different relative measures because the AC voltages are not aligned, i.e. they are out of phase. 208/120V 3? 4W, 120/208V 1? 3W, 480/277V 3? 4W, and 277/480V 1? 3W are common examples.