the neutral passes through the CT cabinet with a main bonding jumper bonding the metal CT cabinet enclosure The equipment grounds originating at the utility company XO land directly to the Ct cabinet enclosure and from their both the neutral(s) and the equipment ground(s) continue on to the service. Am I wrong that current would be found between the larger neutral conductors and the smaller equipment grounds by way of the main bonding jumper and the metal Ct cabinet. I would consider any current on that path as objectionable.
Be sides you may as well call the equipment grounds neutrals when they originate at the XO of the utility transformer when the neutral and the equipment grounds bond together at both the xo and the service enclosure.. In my opinion the circuit current flowing on the equipment grounds as described above during normal conditions is objectionable
Your experience is interesting to me. What you describe, in your posts in this thread, causes me to believe you are talking about, only, certain
Premises Wiring (System) connections to the electric power utility either AT or on the utility side of the
Service Point. I suspect that each specific XO, you are thinking of, with respect to "objectionable current," that you have authority over, is a small group of all of the electric power utility transformers within your jurisdiction.
Can you exert the same control over the utility transformer XO for a grouping of customers connected overhead to a single transformer (120 / 240 single phase) where, because of the distances between buildings, there is utility owned spans of 120 / 240 Volt secondary between several utility owned poles? Let's say there is SINGLE overhead utility primary wire running across the top of all the poles, and this is the source for the single, wye-connected transformer supply to this grouping of customers.
I am not describing an overhead Single Wire Earth Return electric power utility primary distribution to this transformer. The low side of the wye will be bonded to earth at the base of the pole, along with bonding to the transformer can and XO, and along with bonding to the overhead secondary side 120 / 240 Volt grounded conductor which is generally continuous and connected to other groupings of customers connected to other overhead transformers and, ultimately, connected back to the electric power utility substation and yet another transformer. I believe this to be a rather common urban situation. Mix into this scenario, a municipal domestic water system delivered in conductive metal piping to all the customers connected to this one overhead transformer. -------------- The end result --------------- Many parallel paths for unbalance currents from both the customer loads and from the electric power utility primary distribution unbalance. Lets say that most of the homes in this one grouping of customers have fan forced hot air furnaces, each served with a 15 Amp 120 Volt NM-B branch circuit, and the HVAC systems have metal ductwork and are supplied by metal gas piping systems. All the HVAC systems are incidentally connected to Earth and the EGC in the furnace branch circuit is not the sole conductive path to Earth.
Changing the wiring at the overhead transformer XO for this group of customers will affect the "objectionable current".