I'm installing a new production line that was manufactured in Italy. The electrical requirements of the new line are;
400 VAC, 3 Phase, 50Hz, 2500A. They also require a neutral (230VAC) for mostly heating (resistive loads). The total connected load to the neutral is about 1200A but much of this is well balance between all three phases. The actual demand on the neutral should be quite low.
The existing electrical system at our facility consists of a 2000KVA transformer with 34.5 KV (primary delta) and 480 / 277 wye on the secondary. The new equipment can handle the higher voltage on the phases and the frequency should not be a problem either. I am worried about the 277 VAC for the neutral. When our system was installed back in 1985 the neutral from the transformer was never run to the switchgear inside of the building. Unfortunately this is about a 200 foot run underground in 6 - 6"rigid conduits encased in concrete. Getting an additional conductor through the conduits could be quite difficult. I was wondering if a zig zag configuration could be used on a 480/277 system and provide a 230 VAC neutral? I'm a little worried of the 20% increase in voltage for the resistive loads. I would like to drop that by at least 10% or more and get a little closer to the 230V recommended.
400 VAC, 3 Phase, 50Hz, 2500A. They also require a neutral (230VAC) for mostly heating (resistive loads). The total connected load to the neutral is about 1200A but much of this is well balance between all three phases. The actual demand on the neutral should be quite low.
The existing electrical system at our facility consists of a 2000KVA transformer with 34.5 KV (primary delta) and 480 / 277 wye on the secondary. The new equipment can handle the higher voltage on the phases and the frequency should not be a problem either. I am worried about the 277 VAC for the neutral. When our system was installed back in 1985 the neutral from the transformer was never run to the switchgear inside of the building. Unfortunately this is about a 200 foot run underground in 6 - 6"rigid conduits encased in concrete. Getting an additional conductor through the conduits could be quite difficult. I was wondering if a zig zag configuration could be used on a 480/277 system and provide a 230 VAC neutral? I'm a little worried of the 20% increase in voltage for the resistive loads. I would like to drop that by at least 10% or more and get a little closer to the 230V recommended.