mpd

Senior Member
EMT with an equipment ground run from an electrical panel to a disconnect, the EMT is used to ground the disconnect enclosure, the equipment ground from the electrical panel to the equipment is connected to a ground bar in the disconnect that is not bonded to the disconnect enclosure compliant or not code section please
 
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
EMT with an equipment ground run from an electrical panel to a disconnect, the EMT is used to ground the disconnect enclosure, the equipment ground from the electrical panel to the equipment is connected to a ground bar in the disconnect that is not bonded to the disconnect enclosure compliant or not code section please

250.146(D) would be an instance of where it is allowed.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Dennis I think you are correct, that disconnect enclosure would be considered a cutout box
I don't agree that a disconnect switch enclosure is a cutout box. I know that this is something that Mike Holt has taught, but I do not think he is correct.
[h=2]Cabinets and Cutout Boxes, CYIV[/h]GENERAL This category covers sheet-metal boxes and nonmetallic boxes. Cutout boxes are provided with a door secured by hinges and one or more fasteners and are intended for surface mounting. A cabinet consists of two parts: a cabinet box and a mating cabinet front that contains a door. A cabinet may be flush mounted or surface mounted. These boxes are intended for installation in accordance with Article 312 of ANSI/NFPA 70, "National Electrical Code."
 

tkb

Senior Member
Location
MA
EMT with an equipment ground run from an electrical panel to a disconnect, the EMT is used to ground the disconnect enclosure, the equipment ground from the electrical panel to the equipment is connected to a ground bar in the disconnect that is not bonded to the disconnect enclosure compliant or not code section please

It sounds like the solid neutral bar was used and not an equipment ground kit.
There should be a green screw through the solid neutral bar to the enclosure then you would be all set.
 

Smart $

Esteemed Member
Location
Ohio
...that disconnect enclosure would be considered a cutout box
I also disagree, and was thinking such even before I read Don's UL quote. 250.148 covers box grounding only. The metal shell of the disconnect which I believe you are discussing is an enclosure (FWIW the disconnect is likely considered a knife switch under Code).

For an enclosure, 250.134 applies, but does not specifically say where the raceway qualifies as an EGC, a redundant wire-type EGC must also be bonded where run in the raceway.

I conclude bonding the grounding bar to the disconnect enclosure is not required as it is with boxes.
 

jusme123

Senior Member
Location
NY
Occupation
JW
It sounds like the solid neutral bar was used and not an equipment ground kit.
There should be a green screw through the solid neutral bar to the enclosure then you would be all set.

No, the neutral gets bonded at one point only, usually at service, from there on it should remain isolated from ground.
 

Smart $

Esteemed Member
Location
Ohio
No, the neutral gets bonded at one point only, usually at service, from there on it should remain isolated from ground.
I think he's saying the installer may have used the disconnect's neutral feed-through bus as an EGC feed-through bus... and it could be bonded to the enclosure by using the green screw (only if an SUSE disconnect).
 

tkb

Senior Member
Location
MA
No, the neutral gets bonded at one point only, usually at service, from there on it should remain isolated from ground.

I think he's saying the installer may have used the disconnect's neutral feed-through bus as an EGC feed-through bus... and it could be bonded to the enclosure by using the green screw (only if an SUSE disconnect).

Yes, I meant that the installer used the solid neutral bar as an equipment ground bar. When doing this the green screw must be used.
 

Carultch

Senior Member
Location
Massachusetts
Not likely, but legal.

Just pointing out that an isolated ground is not a code violation. I have installed lathes in Machine shops that wanted an isolated EG. They got one. The conduit was also a suitable EG.


How exactly would you get an isolated EGC? Isolated from what, exactly so?

Metal conduit gets you a continuous path from origin enclosure to destination enclosure, and at the origin enclosure, the premises EGC bar is built in, and electrically continuous with the enclosure. And that would be where I'd be deriving this "isolated" EGC.

If I take an Ohm-meter across both the separate EGC, and the destination enclosure, I will get a continuity buzz. That is anything but isolated.

What would such a machine require you to do? Put in a special grounding reactor between the isolated EGC and the general EGC?
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
How exactly would you get an isolated EGC? Isolated from what, exactly so?

Metal conduit gets you a continuous path from origin enclosure to destination enclosure, and at the origin enclosure, the premises EGC bar is built in, and electrically continuous with the enclosure. And that would be where I'd be deriving this "isolated" EGC.

If I take an Ohm-meter across both the separate EGC, and the destination enclosure, I will get a continuity buzz. That is anything but isolated.

What would such a machine require you to do? Put in a special grounding reactor between the isolated EGC and the general EGC?

Isolated, in this context ONLY means isolated back to the single point where the EGC wires and the service or SDS neutral are bonded.

What it gives you is a ground reference to that specific point between the EGC network and the GES without the voltage offset (particularly at high frequencies) that may be caused by leakage current traveling over the primary EGC path (branch and feeder combined) feeding that branch and specific outlet wiring.
 

MasterTheNEC

CEO and President of Electrical Code Academy, Inc.
Location
McKinney, Texas
Occupation
CEO
I don't agree that a disconnect switch enclosure is a cutout box. I know that this is something that Mike Holt has taught, but I do not think he is correct.
I agree with this statement. The term cutout box doesn't default to mean a disconnect switch. However, a disconnect switch (knife, CB or otherwise) can be installed in a Cabinet or Cutout Box. Both of which are described in Article 100.
 