Pierre C Belarge
Senior Member
- Location
- Westchester County, New York
Did you notice the first picture? The contractor supported the box to wood that has been support to another piece of 2 x 4 - which I believe is supported to a wall stud.
don_resqcapt19 said:Pierre,
It doesn't appear that would be permitted by 314.23, but I have never seen any other support used for a box in a masonry surface.
Don
One of the problems with using the handbook on the computer...sometimes when I come to the comment section, I don't scroll down.314.23(G),Enclosures in Concrete or Masonry "An enclosure supported by embedment shall be identified as suitably protected from corrosion and securely embedded in concrete or masonry."
don_resqcapt19 said:Michael,
One of the problems with using the handbook on the computer...sometimes when I come to the comment section, I don't scroll down.
Don
Doesn't the buildnig code have a general requirement that any wood in contact with masonry be pressure treated?Pierre C Belarge said:Did you notice the first picture? The contractor supported the box to wood that has been support to another piece of 2 x 4 - which I believe is supported to a wall stud.
It's moot because the NM shouldn't be there in the first place, but Halex 3/8" are rated for two 14/2s but only one 12/2.mdshunk said:You'd have to. I don't think there are any on the market now that aren't so rated.Originally Posted by LawnGuyLandSparky
..., and 2 NM cables under one connector, though I'd let that slide.
tallguy said:It's moot because the NM shouldn't be there in the first place, but Halex 3/8" are rated for two 14/2s but only one 12/2.
Pierre C Belarge said:Do you install a box on the exterior wall of a wood framed house to supply an outside light fixture, using NM cable? Or do you supply those light fixtures with UF cable?
NM, but I can see an argument against that.Pierre C Belarge said:Do you install a box on the exterior wall of a wood framed house to supply an outside light fixture, using NM cable? Or do you supply those light fixtures with UF cable?
I was referring to this pic, not the first one, since it is the only one with two pieces of NM on it:stickboy1375 said:I was wondering myself were Tallguy was going with that comment...
cschmid said:#2 & #3 lets see nm exposed to moist conditions even inside of conduit.
I'm with LawnGuy and cschmid.LawnGuyLandSparky said:NM cable in wet location.
Oh yeah, and Ryan too.ryan_618 said:...the NM cable is a violation in pictures 2 and 3.
tallguy said:Maybe I've been caught up in all this "interior of a wet enclosure/raceway in a wet location is considered wet as well" talk we've had recently? Doesn't look like a dry location to me, therefore no NM. To my eye this is different than Pierre's scenario listed above...
No... talking about Pierre's photos of a stone wall....stickboy1375 said:So are you calling the interior of your walls a wet location?
cschmid said:with the box in concrete and on the exterior wall it will sweet with temp changes and it wont care if it is rated for the use..so the paper wrap will definitely take on moisture over time..whether it does any damage in a reasonable period of time is the question? Has anyone ever tested it to see how long it takes for nm exposed to the weather to deteriorate?